Need to clarify something on your posted question.
Are you trying to get two 60 Volt 2 wire (or a 60/120 Volt 3 wire) outputs from this Transformer, or just a simple 120/240 VAC 1Ø 3 Wire output?
You can do the 120/240 VAC 1Ø 3 Wire setup by connecting X2 and X3 in Series, then "Tapping" this jumpered connection (at either X2 or X3), which will result in the Center Tapped Neutral conductor.
Voltage will be 120 VAC between X1 or X4 and the center tapped conductor, and 240 VAC from X1 to X4.
Unless this Transformer's Secondary has multiple taps on each Split Coil, you cannot get an output of 60 VAC from any two "X" points.
It sounds like a Split Coil Primary + Split Coil Secondary isolation Transformer - the common types used in "Buck-Boost" setups.
The Primary has 4 "H" terminals (H1, H2, H3, H4). For an input voltage of 240 VAC, H1 and H3 get connected together, H2 and H4 connect together (Parallel connection), and input goes on H1 and H4.
For an input of 480 VAC, only one jumper is used, which is placed between H2 and H3 (Series Additive connection) and input lands on H1 and H4.
Similar connections for the Secondary coils - 240 VAC output uses one jumper, connecting X2 and X3 in Series additive. 240 VAC output is between X1 and X4.
(this can also be the center tapped scheme I described before).
And, for an output of 120 VAC, X1 + X3 get connected, and X2 + X4 get connected (Parallel scheme).
120 VAC output is across X1 and X4.
As to the Apparent Power ratings of Split Coil Transformers, the combination of both Windings is where the ratings are applied.
For example, if the Transformer's Power rating is 10 KVA, each coil has a rating of only 5 KVA.
Let me know if I have mistakenly read your post, and if you have questions.
Scott35