Scott, Doug's intention is to connect the primaries in series, i.e., for 480v, and then connect them to 240v, which will result in the secondaries to produce half voltage.

He then wants to connect the secondaries in series also, resulting in 120v with center tap from what would normally be 240v w/center tap, ending up with 2 x 60v. outputs.

He's concerned with the resulting available VA. Well, I'd say that Ian is correct: the same secondary current, at half the voltage, will result in half the KVA.

Doug, keep in mind that you can also use the secondaries individually or in parallel. If the two 60v loads are evenly divisible, you can series them for 120v use.

This would allow you to parallel both the primaries and the secondaries, again running the loads in series, and getting the full 25 KVA capacity.


Larry Fine
Fine Electric Co.