The major limiting factors on a transformer are wire size and the core area. The wire size limits the current you can draw and the KVA is limited by the core area so: 25Kva/240 volt secondary=104.1666 amps Theoretically if you keep the 60V load at that limit or less (104Amps) you should be fine as the lower voltage will keep you well within the power limits of the core. P=IE 120V*104A=12,480 KVA