I can see how Wiggy tests would be a decent go, no-go test of GFCI function. I always use meters and the datasheet I just d/l'd for the Wiggy, doesn't list input resistance. Unless it's substantially higher than 20 kohm, it is faulting too much current to verify that the GFCI is operating within spec. I'll be using a pot in series with a current limiting resitor to fault current to ground through my Fluke. It will be on AC mA & min/max record. I'll start at 110K and ramp down till it trips and read max off of the meter. I'll start with the fault current being the only load and step in increasing l-n loads to see if fault sensitivity changes.

I'm also going to borrow a Wiggy from one of our electricians for a few minutes and see how much fault current it will flow @ 120V.
Joe