OK, here is something a little more solid.

If you did extend the circuit ungrounded, you couldn't install a 2-wire receptacle. Otherwise you would violate 406.3 (A). A new circuit must have grounded receptacle, it is not a "replacement" situation.

Bottom line: for a non-grounded BC extension, you must install a grounded-type receptacle, and the EGC must be connected per 250.130(C).


Peter