Unfortunately, you can't extend an ungrounded circuit, so you have created a violation there.

For this circuit to be code compliant, you must run a separate EGC back to a code compliant location. After you run the EGC, the GFCI isn't necesary unless it's in a location that requires one.

The GFCI will still function without the EGC.

The plug-in testers shunt the leakage current to ground, and since you don't have one, that's why it won't trip with it.