Make every effort to get the numbers from the POCO. They do have them.

We got scr--ed bad once. We made calculations for a 600A 208Y/120 3PH system for an office building fed from a dedicated pad mount transformer. Not taking many chances we installed 42K equipment (225KVA, 625A, 1.5%Z). When the inspector called the POCO for their fault level they said 65K because, during an emergency, they might choose to install a larger transformer.