Hey guys, thanks for the thoughts.
Hotline,
I have a book "Short Circuit Calculations 'The Easy Way'" Published by EC&M Books. It came with a 3.5" floppy. I've had it for some time and just haven't gotten a chance to open it. Thanks for the Bussman reference.
GamecockEE,
so in your example 112.5kva with 2% impedence,
[112500/(1.73*208)]=312 amps
312*100=31,200
31,200/2=15,600
or
31,200/.02=1,560,000?
I take it 15,600 right?
What do I do if there are 3 cans up on the pole, add the ratings of eack can together? The reason this caught my eye in the first place was that there is only 15' of service drop, so I knew that would play a little less of role in reducing the fault current.
Bjarney & Ron,
I did consider doing exactly that, going to a fused disconnect with class T fuses. I had a real good inspector a couple of years back require (or suggest I can't remember) that because of a 25K AFC on a service change. It was actually that job that really clued me in on this being a part of my job that I should pay closer attention to. Although since then I've learned about series ratings and now I'm not too sure how that factors in.
Besides, I don't even know yet what the AFC is, and I'm afraid that by the time I find out, they are going to be staring at me asking when they can open. I just hope the answer isn't "3 weeks to get the parts, and a day to put it in"
Alright, one last vent. I guess my delemma is this:
My gut has not been thouroghly trained to look up at transformer and say either, "nothing to worry about, looks close better run some numbers, or I know that's over 22K, better run some numbers to see how far over". Since there is no EE on this, I will have to run the numbers anyway just to cover myself, that is if I can get some cooperation. In the mean time, I have the GC and his big timer saying I'm wasting time even worrying about it.
Well I guess that's it, I'll just have to read this book, crunch the numbers myself, and hope for the sake of my own ego that it comes in over 22K, order the 65K main, and tell everybody see told you so and here's your extra for the engineering.
thanks for listening