One last point:

Breakers used to feed motors are sized to withstand the inrush current that they draw.

This means that, unlike resistive loads, the running current from a breaker to a motor load will typically be about half of the nominal breaker rating.

e.g. a 35A 2-pole breaker will be mated to a motor that draws 17 A in normal, full-load service.

So, the customer's feeder conductors are even more conservatively sized than the above, quick-snap calculation implies.

=========

His actual running loads are not even tapping half the available feeder current -- almost certainly.

Last edited by Tesla; 12/23/12 08:57 PM.

Tesla