Interesting point to add:

Per PSE&G Green Book (POCO REquirements)

Unguyed service mast is acceptable with a max height above 'highest support' to the point of attachment for size 2/0 or smaller service drop wires....

2" conduit, max height 2 feet
2-1/2" conduit, max height 4 feet
3" conduit, max height 7 feet

note 5: When back guying is required for heights exceeding those listed above, the following requirements shall apply:
- Guy shall be securely fastened to anchored stud
- Guy wire shall be minimum 1/4" galv. wire.
PSE&G assumes no responsibility for building damage associated with this type of construction.

That's a CYA for sure!

On the drawing (Exibit 4) a Minimum of two (2) supports (straps) are required above the meter pan 'with 1/2" machine thru bolts through wall studs; capable of withstanding a 1000 lb horizontal pull.

I'll see if I can scan the pages from the book soon.

Book is 2005, so there may be some changes. Mast services are not common in my twp.



John