239 volts, single phase, 15KW load, equates to 69.7 amps of load. That (69.7) is approx. 15% overload by math. Hence, over a period of time....the CB will fail. You need a minimum 90 amp cb! Perhaps the first person that replaced the CB saw "60" instead of "90"??



John