In this discussion do not forget that in certain power grids a protection in case of an isolation fault can only be realized by means of an RCD because the loop impedance is to high. In typical TT-systems (France, Belgium for instance) earth leakage even in case of a full short to earth is that weak that a fuse will never trip.

That's why in France RCD's are usually integrated in the mains switch delivered by the PoCo.

So the RCD discussion is not the same for everybody.