Is this a TT system? Has the earth wire somehow been disconnected from the earth electrode? An phase-earth leak (or direct short circuit) after the 30 mA RCD would not be noticed by the RCD if there is no connection to the earth electrode. It would go away when you switch off this RCD or the breakers under it. It sounds odd though, as one would expect some connection through appliances.