Correct - as Bjarney mentions I was refering to a 3Ø 4 Wire Delta - with Center Tapped winding, of the "Double Voltage" family.

I found 240 VAC on two of the three Phase Lines - as measured L-G, and on one Phase Line, found "More Than 240 VAC to Ground" - and since this smells "Delta-Ish", one could figure the Voltage to Ground on that single Maverick Phase Line to be in the area of 415.68 VAC
(240 × 1.732)

First thing I was thinking when there was a Voltage to Ground measured (with a Wiggy), was a Wye setup - having the Common Star Point Grounded. Finding >240 VAC to Ground on one Phase Line was totally unexpected, and debunked the Wye concept!

This was a nice "Whaddaheck" experience to me, as it was so totally unexpected!
(however, the guy I was working with found this to be of no interest, which really bummed me out!).