One reason for using 480V center-tap-grounded service is to “skirt” around NEC 230-95 ground-fault-protection. It’s a poor compromise, for you also lose the ability to use ‘slash-rated’ 480Y/277V circuit breakers and 300-volt fuses. The capability for arcing-ground-fault damage compared to 480V grounded-wye service is essentially the same.