The two violations:

1. Insufficient EMT bend radius.
2. Conduit installation likely not completed prior to installation of wires.

And at least five, and maybe seven more in the upper photo:

3. Improper connector at box (not for EMT).
4. Exposed wires to lighting fixture.
5. Lighting fixture not listed for direct surface mounting.
6. Insufficient NM bend radius (into hole in soffit).
7. NM not secured within 12" of box.

If this is considered a wet location:

8. NM not allowed in wet location.
9. Non-weathertight box in wet location.

Did I miss anything?