The white conductors on the load side terminals is a violation of Article 200.7
The green conductor on the line side violates Art. 400.23 and 310.12(B)&(C)
The red conductor as EGC violates Art. 250.119 and the manner in which it is attached violates 250.148.
The lack of a fitting on the cable violates Art. 400.14
I don't have any more time right now, maybe there's more.

[This message has been edited by Redsy (edited 06-05-2002).]