I’m not getting any responses so far. Hope I explained situation clearly. This motor disconnect was wired with, what I call, a male connector or receptacle. The color coding on the wires (pig-tail) from this male receptacle into disconnect were o.k.. I think the power conductors were all black and the ground was green. So when you plugged the female end of the 50 ft. cable into disconnect’s male receptacle, wiring to the observer appeared to be code compliant. No one ever knew that internally the cable had a green wire caring 480v and a red conductor was a ground. And we would never of known had we not been forced, by circumstances, to cut off the cable’s female end and wire it directly to motor disconnect.
Is the manufacturer of this cable suppose to follow the NEC?
We tried to pull the end connector off the new cable we received, to replace the one pictured above, but couldn’t without damaging or destroying new cable. So how do you check the wiring?
We were told the cable manufacturer was notified of what we found.