Metalic Raceway Grounding #93494
05/28/05 07:36 PM
05/28/05 07:36 PM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 608
massachusetts
I have been installing PVC underground to supply outdoor branch circuits. PVC makes for a speedy installation.

I have had some of this PVC damaged from impact, including SCH 80 where it emerges from ground.

I want to use a piece of ridged conduit only where it emerges from ground and change right back to PVC.

Does the code require this short section used for physical protection to be bonded to the grounding conductor of the branch circuit?

shortcircuit

2017 / 2014 NEC & Related Books and Study Guides
Re: Metalic Raceway Grounding #93495
05/28/05 08:28 PM
05/28/05 08:28 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Yes.


Joe Tedesco, NEC Consultant
Re: Metalic Raceway Grounding #93496
05/28/05 09:05 PM
05/28/05 09:05 PM
G
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
I can never find this code article when I need it, including now, but Joe is right. If you use a short piece of rigid in a run of PVC (some guys like to use rigid 90's including me) the only way it doesn't need bonding is to be 24" or more underground.

Re: Metalic Raceway Grounding #93497
05/28/05 10:34 PM
05/28/05 10:34 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
See 250.80, Exception, and 250.86, Exception No. 3


Joe Tedesco, NEC Consultant
Re: Metalic Raceway Grounding #93498
05/28/05 10:55 PM
05/28/05 10:55 PM
G
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
Oops. 18".

Re: Metalic Raceway Grounding #93499
05/28/05 11:32 PM
05/28/05 11:32 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,165
Estero,Fl,usa
Can you drop a short sleeve of RMC over the PVC where it is subject to "severe" damage.


Greg Fretwell
Re: Metalic Raceway Grounding #93500
05/29/05 12:34 AM
05/29/05 12:34 AM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Greg- I like that idea of slipping a piece of RMC or IMC over the PVC. And you wouldn't even have to bond it [Linked Image]


George Little
Re: Metalic Raceway Grounding #93501
05/29/05 04:56 AM
05/29/05 04:56 AM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 608
massachusetts
gfretwell...I too, like that sleeve idea and will try it!

250.86 exception #2 allows short sections of metalic raceway to be ungrounded where used to protect cable assemblies...

So, if it where UF wire emerging from ground, then no bonding...

But, if the raceway encloses individual conductors for the branch circuit, then bonding is required...

Do we agree?

shortcircuit

Re: Metalic Raceway Grounding #93502
05/29/05 08:48 AM
05/29/05 08:48 AM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
I asked an EC for that same idea. He had an underground 400 amp service and where the pipe came up through the floor in the basement, he sleeve the PVC riser with Ridgid and he didn't have to worry about his kids ( or anyone else) hitting the PVC riser and cracking the pipe. I think this guy went even one better and stuck some concrete inside of the RMC.

Re: Metalic Raceway Grounding #93503
05/29/05 12:14 PM
05/29/05 12:14 PM
A
Active 1  Offline
Member
Joined: Feb 2003
Posts: 687
Grayslake IL, USA
What is the advantage Of sleving the PVC with RMC compared to using only RMC at the stub up? I seen it specked out but just never seen any advantage.

Tom

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 19
Potseal 13
Popular Topics(Views)
243,512 Are you busy
180,304 Re: Forum
170,802 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.049s Queries: 15 (0.022s) Memory: 1.0216 MB (Peak: 1.1997 MB) Zlib enabled. Server Time: 2018-01-16 17:36:11 UTC