Metalic Raceway Grounding #93494 05/28/05 08:36 PM
Joined: Jun 2004
Posts: 613
S
shortcircuit Offline OP
Member
I have been installing PVC underground to supply outdoor branch circuits. PVC makes for a speedy installation.

I have had some of this PVC damaged from impact, including SCH 80 where it emerges from ground.

I want to use a piece of ridged conduit only where it emerges from ground and change right back to PVC.

Does the code require this short section used for physical protection to be bonded to the grounding conductor of the branch circuit?

shortcircuit

2017 / 2014 NEC & Related Books and Study Guides
Re: Metalic Raceway Grounding #93495 05/28/05 09:28 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline
Member
Yes.


Joe Tedesco, NEC Consultant
Re: Metalic Raceway Grounding #93496 05/28/05 10:05 PM
Joined: Mar 2005
Posts: 212
G
Gregtaylor Offline
Member
I can never find this code article when I need it, including now, but Joe is right. If you use a short piece of rigid in a run of PVC (some guys like to use rigid 90's including me) the only way it doesn't need bonding is to be 24" or more underground.

Re: Metalic Raceway Grounding #93497 05/28/05 11:34 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline
Member
See 250.80, Exception, and 250.86, Exception No. 3


Joe Tedesco, NEC Consultant
Re: Metalic Raceway Grounding #93498 05/28/05 11:55 PM
Joined: Mar 2005
Posts: 212
G
Gregtaylor Offline
Member
Oops. 18".

Re: Metalic Raceway Grounding #93499 05/29/05 12:32 AM
Joined: Jul 2004
Posts: 9,513
G
gfretwell Offline
Member
Can you drop a short sleeve of RMC over the PVC where it is subject to "severe" damage.


Greg Fretwell
Re: Metalic Raceway Grounding #93500 05/29/05 01:34 AM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
Greg- I like that idea of slipping a piece of RMC or IMC over the PVC. And you wouldn't even have to bond it [Linked Image]


George Little
Re: Metalic Raceway Grounding #93501 05/29/05 05:56 AM
Joined: Jun 2004
Posts: 613
S
shortcircuit Offline OP
Member
gfretwell...I too, like that sleeve idea and will try it!

250.86 exception #2 allows short sections of metalic raceway to be ungrounded where used to protect cable assemblies...

So, if it where UF wire emerging from ground, then no bonding...

But, if the raceway encloses individual conductors for the branch circuit, then bonding is required...

Do we agree?

shortcircuit

Re: Metalic Raceway Grounding #93502 05/29/05 09:48 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
I asked an EC for that same idea. He had an underground 400 amp service and where the pipe came up through the floor in the basement, he sleeve the PVC riser with Ridgid and he didn't have to worry about his kids ( or anyone else) hitting the PVC riser and cracking the pipe. I think this guy went even one better and stuck some concrete inside of the RMC.

Re: Metalic Raceway Grounding #93503 05/29/05 01:14 PM
Joined: Feb 2003
Posts: 687
A
Active 1 Offline
Member
What is the advantage Of sleving the PVC with RMC compared to using only RMC at the stub up? I seen it specked out but just never seen any advantage.

Tom

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
268,614 Are you busy
202,965 Re: Forum
191,341 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3