#89057 - 08/26/04 09:21 PM ENT ALLOWED in MEDICAL FACILITY?  
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
forgot to ask, is ent allowed in a clinic?


Electricity has no respect for ignorance!

2017 / 2014 NEC & Related Books and Study Guides

#89058 - 08/26/04 09:56 PM Re: ENT ALLOWED in MEDICAL FACILITY?  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Not in the areas that require redundant grounding. Also remember that FMC over 6’ is not permitted. You really only have 2 options, a metal raceway (RMC, IMC or EMT) with separate insulated ground wire or HCF AC cable.


Curt Swartz

#89059 - 08/26/04 10:11 PM Re: ENT ALLOWED in MEDICAL FACILITY?  
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
thanks, you can always rely on good information from the members of this site..recently was hired to help a contractor out of trouble with a couple jobs..i thought ent and bx looked funny for some reason and ENT WAS longer than 6 feet to boot!

80% of 6000 sq foot of building was ready for rough-in..told boss that there was problem...he decided to fire me...i decided to call the state and ask them who was right..

boss should have taken two and thought it through..

inspectors shut em down for using bx and ent

not a license on the job even though required..

i resigned way before he decided to fire me for questioning his knowledge!

i wonder what he will do now? i am surprised he did not do it in romex!

the cost of that job just doubled...

sad situation these days..



[This message has been edited by mustangelectric (edited 08-26-2004).]


Electricity has no respect for ignorance!

#89060 - 08/31/04 05:56 AM Re: ENT ALLOWED in MEDICAL FACILITY?  
zapped208  Offline
Member
Joined: Feb 2003
Posts: 196
Somewhere in USA
You guys should read Article 362....ENT


Shoot first, apologize later.....maybe

#89061 - 08/31/04 11:05 AM Re: ENT ALLOWED in MEDICAL FACILITY?  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Zapped,
I could read Article 362 a thousand times but ENT will not meet the redundant grounding requirements of Article 517.


[This message has been edited by caselec (edited 08-31-2004).]


Curt Swartz

#89062 - 08/31/04 12:41 PM Re: ENT ALLOWED in MEDICAL FACILITY?  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,076
Estero,Fl,usa
You can't concentrate too much on "redundant ground". That could just be two green wires.
The fact is 517 says one of these grounds will be the "metal" wiring method itself.

517.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas.
Wiring in patient care areas shall comply with 517.13(A) and (B).
(A) Wiring Methods. All branch circuits serving patient care areas shall be provided with a ground path for fault current by installation in a metal raceway system, or a cable armor or sheath assembly. The metal raceway system, or cable armor, or sheath assembly, shall itself qualify as an equipment grounding return path in accordance with 250.118. Type AC, Type MC, Type MI cables shall have an outer metal armor or sheath that is identified as an acceptable grounding return path.
(B) Insulated Equipment Grounding Conductor...

Sort of eliminates any plastic wiring method huh?


Greg Fretwell

#89063 - 08/31/04 07:03 PM Re: ENT ALLOWED in MEDICAL FACILITY?  
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
Is it allowed in non patient areas? 517-10.


#89064 - 08/31/04 08:03 PM Re: ENT ALLOWED in MEDICAL FACILITY?  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Trekkie, yes it is allowed in "Non Patient Care Areas" specifically per 517-12, which would also allow NM or any other wiring method in chapter 3.

Out of curiosity, is your area still under an NEC cycle pre 2002?

Roger


#89065 - 08/31/04 08:44 PM Re: ENT ALLOWED in MEDICAL FACILITY?  
zapped208  Offline
Member
Joined: Feb 2003
Posts: 196
Somewhere in USA
Guys, I was meaning non patient care areas too mustang's post.
I have pulled my share of HCF/M/C cable.


Shoot first, apologize later.....maybe

#89066 - 09/01/04 04:15 PM Re: ENT ALLOWED in MEDICAL FACILITY?  
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
Roger, we are on 2002 NEC up here in the sticks


Page 1 of 2 1 2

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 15 (0.003s) Memory: 0.8170 MB (Peak: 0.9890 MB) Zlib enabled. Server Time: 2017-05-23 20:45:09 UTC