wireway #87648
04/01/04 08:26 PM
04/01/04 08:26 PM
B
big guy  Offline OP
Member
Joined: Dec 2003
Posts: 59
pa
I have seen this done and can't find any
violations.Can you put EMT through a wireway
at a right angle
Example
If i have a panel with a wireway above it (horizontal)can i run EMT Vertically through
the wireway right into the panel.
thanks big guy

2017 / 2014 NEC & Related Books and Study Guides
Re: wireway #87649
04/02/04 05:06 AM
04/02/04 05:06 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I do not know any violation with that.

Looks bad but sometimes the only option.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: wireway #87650
04/03/04 09:39 PM
04/03/04 09:39 PM
P
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
725.55(C) permits raceways within enclosures. I do not see where this is prohibited, and as Bob has said may be the only way to reach a panel.

Pierre


Pierre Belarge
Re: wireway #87651
04/04/04 12:04 AM
04/04/04 12:04 AM
S
stamcon  Offline
Member
Joined: Mar 2001
Posts: 330
So San Francisco CA


Steve
Re: wireway #87652
04/06/04 04:58 PM
04/06/04 04:58 PM
B
big guy  Offline OP
Member
Joined: Dec 2003
Posts: 59
pa
yes that is what i has talking about
Would you use the O.D of the pipe as your
20%. 376.22 02 code thanks

Re: wireway #87653
04/09/04 10:48 AM
04/09/04 10:48 AM
C
Cobtronics  Offline
Member
Joined: Jul 2003
Posts: 18
Vermont
We do this all the time in the plant I'm in. Many advantages: 1)Makes for a snap to add new pipes in limited spaces. 2) Can run new pipe and wire into gutter w/o shutting down the panel - only shut down for final pull and connect. 3) You run outta KOs on the top fast and the pipe job gets ugly when you have to snake 15 - 20 runs into the side KOs - even pull ells don't help sometimes. On jobs where this wasn't done, the panel top might have been made of chicken wire for all the strength it had after it was punched.
We deduct the volume of the pass thrus from the volume of the box for fill calcs, but that is the engineer's or AHJ's call to make initially.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,561 Are you busy
180,362 Re: Forum
170,840 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.9741 MB (Peak: 1.1200 MB) Zlib enabled. Server Time: 2018-01-20 11:00:57 UTC