1 members (gfretwell), 231 guests, and 9 robots.
#87648 04/01/04 09:26 PM
big guy Offline OP
I have seen this done and can't find any
violations.Can you put EMT through a wireway
at a right angle
Example
If i have a panel with a wireway above it (horizontal)can i run EMT Vertically through
the wireway right into the panel.
thanks big guy
Workgear for Electricians
#87649 04/02/04 06:06 AM
I do not know any violation with that.
Looks bad but sometimes the only option.
#87650 04/03/04 10:39 PM
725.55(C) permits raceways within enclosures. I do not see where this is prohibited, and as Bob has said may be the only way to reach a panel.
Pierre
Pierre Belarge
#87651 04/04/04 01:04 AM
Steve
#87652 04/06/04 05:58 PM
big guy Offline OP
yes that is what i has talking about
Would you use the O.D of the pipe as your
20%. 376.22 02 code thanks
#87653 04/09/04 11:48 AM
We do this all the time in the plant I'm in. Many advantages: 1)Makes for a snap to add new pipes in limited spaces. 2) Can run new pipe and wire into gutter w/o shutting down the panel - only shut down for final pull and connect. 3) You run outta KOs on the top fast and the pipe job gets ugly when you have to snake 15 - 20 runs into the side KOs - even pull ells don't help sometimes. On jobs where this wasn't done, the panel top might have been made of chicken wire for all the strength it had after it was punched.
We deduct the volume of the pass thrus from the volume of the box for fill calcs, but that is the engineer's or AHJ's call to make initially.