wireway #87648 04/01/04 08:26 PM
Joined: Dec 2003
Posts: 59
B
big guy Offline OP
Member
I have seen this done and can't find any
violations.Can you put EMT through a wireway
at a right angle
Example
If i have a panel with a wireway above it (horizontal)can i run EMT Vertically through
the wireway right into the panel.
thanks big guy

2017 / 2014 NEC & Related Books and Study Guides
Re: wireway #87649 04/02/04 05:06 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
I do not know any violation with that.

Looks bad but sometimes the only option.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: wireway #87650 04/03/04 09:39 PM
Joined: Jun 2003
Posts: 681
P
PCBelarge Offline
Member
725.55(C) permits raceways within enclosures. I do not see where this is prohibited, and as Bob has said may be the only way to reach a panel.

Pierre


Pierre Belarge
Re: wireway #87651 04/04/04 12:04 AM
Joined: Mar 2001
Posts: 333
S
stamcon Offline
Member


Steve
Re: wireway #87652 04/06/04 04:58 PM
Joined: Dec 2003
Posts: 59
B
big guy Offline OP
Member
yes that is what i has talking about
Would you use the O.D of the pipe as your
20%. 376.22 02 code thanks

Re: wireway #87653 04/09/04 10:48 AM
Joined: Jul 2003
Posts: 18
C
Cobtronics Offline
Member
We do this all the time in the plant I'm in. Many advantages: 1)Makes for a snap to add new pipes in limited spaces. 2) Can run new pipe and wire into gutter w/o shutting down the panel - only shut down for final pull and connect. 3) You run outta KOs on the top fast and the pipe job gets ugly when you have to snake 15 - 20 runs into the side KOs - even pull ells don't help sometimes. On jobs where this wasn't done, the panel top might have been made of chicken wire for all the strength it had after it was punched.
We deduct the volume of the pass thrus from the volume of the box for fill calcs, but that is the engineer's or AHJ's call to make initially.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,206 Are you busy
206,090 Re: Forum
194,096 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3