#87648 04/01/04 09:26 PM
Joined: Dec 2003
Posts: 59
B
big guy Offline OP
Member
I have seen this done and can't find any
violations.Can you put EMT through a wireway
at a right angle
Example
If i have a panel with a wireway above it (horizontal)can i run EMT Vertically through
the wireway right into the panel.
thanks big guy

Horizontal Ad
#87649 04/02/04 06:06 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
I do not know any violation with that.

Looks bad but sometimes the only option.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#87650 04/03/04 10:39 PM
Joined: Jun 2003
Posts: 681
P
Member
725.55(C) permits raceways within enclosures. I do not see where this is prohibited, and as Bob has said may be the only way to reach a panel.

Pierre


Pierre Belarge
#87651 04/04/04 01:04 AM
Joined: Mar 2001
Posts: 333
S
Member


Steve
#87652 04/06/04 05:58 PM
Joined: Dec 2003
Posts: 59
B
big guy Offline OP
Member
yes that is what i has talking about
Would you use the O.D of the pipe as your
20%. 376.22 02 code thanks

#87653 04/09/04 11:48 AM
Joined: Jul 2003
Posts: 18
C
Member
We do this all the time in the plant I'm in. Many advantages: 1)Makes for a snap to add new pipes in limited spaces. 2) Can run new pipe and wire into gutter w/o shutting down the panel - only shut down for final pull and connect. 3) You run outta KOs on the top fast and the pipe job gets ugly when you have to snake 15 - 20 runs into the side KOs - even pull ells don't help sometimes. On jobs where this wasn't done, the panel top might have been made of chicken wire for all the strength it had after it was punched.
We deduct the volume of the pass thrus from the volume of the box for fill calcs, but that is the engineer's or AHJ's call to make initially.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Top Posters(30 Days)
Popular Topics(Views)
352,506 Are you busy
276,174 Re: Forum
255,655 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5