Transformer as a raceway? #80760
05/15/02 02:28 PM
05/15/02 02:28 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Question from:

Theodore P. Von Sydow
US. Department of State

My question in a nutshell: Can a conductor pass through a transformer if it is not connected to the transformer?

Can the transformer be used as a raceway for a circuit or conductor that is not directly related to the function of the transformer?

Thank you


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Transformer as a raceway? #80761
05/15/02 07:40 PM
05/15/02 07:40 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
If there is no violation of voltage class' of insulation, or type of wiring (communications, fire alarm, etc), seems ok.


Ron
Re: Transformer as a raceway? #80762
05/16/02 06:20 AM
05/16/02 06:20 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
This is not a good practice.
If the transformer fails, you would have to remove the conductor and disrupt it's loads in order to replace the transformer.

Re: Transformer as a raceway? #80763
05/16/02 07:47 AM
05/16/02 07:47 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
I agree, no foreign wires are to be passed through the transformer. I expect that there will be many who wear the AHJ hat that will agree. It is also common knowledge that all conductors are not to be passed through an area that originates in the top section -- the label in the transformer enclosure will cleary identify this and other restrictions.


Joe Tedesco, NEC Consultant
Re: Transformer as a raceway? #80764
05/16/02 10:39 PM
05/16/02 10:39 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
I also agree, not a good practice. I think the original questions infers that the poster wants to know if it is a code violation. I don't find a violation.


Ron

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,581 Are you busy
180,379 Re: Forum
170,855 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.004s) Memory: 0.9662 MB (Peak: 1.1065 MB) Zlib enabled. Server Time: 2018-01-21 18:06:50 UTC