ECN Forum
Posted By: Joe Tedesco Transformer as a raceway? - 05/15/02 07:28 PM
Question from:

Theodore P. Von Sydow
US. Department of State

My question in a nutshell: Can a conductor pass through a transformer if it is not connected to the transformer?

Can the transformer be used as a raceway for a circuit or conductor that is not directly related to the function of the transformer?

Thank you
Posted By: Ron Re: Transformer as a raceway? - 05/16/02 12:40 AM
If there is no violation of voltage class' of insulation, or type of wiring (communications, fire alarm, etc), seems ok.
Posted By: Redsy Re: Transformer as a raceway? - 05/16/02 11:20 AM
This is not a good practice.
If the transformer fails, you would have to remove the conductor and disrupt it's loads in order to replace the transformer.
Posted By: Joe Tedesco Re: Transformer as a raceway? - 05/16/02 12:47 PM
I agree, no foreign wires are to be passed through the transformer. I expect that there will be many who wear the AHJ hat that will agree. It is also common knowledge that all conductors are not to be passed through an area that originates in the top section -- the label in the transformer enclosure will cleary identify this and other restrictions.
Posted By: Ron Re: Transformer as a raceway? - 05/17/02 03:39 AM
I also agree, not a good practice. I think the original questions infers that the poster wants to know if it is a code violation. I don't find a violation.