#5043 - 10/30/01 01:30 PM didn't pass inspection, your thoughts  
electricj  Offline
Member
Joined: Aug 2001
Posts: 10
Boston, MA, USA
I did a service last week (hadn't done one in 8 years prior) I had pounded in a ground rod by the meter and ran a ground wire into the meter. I was told to come back and run the wire inside a pipe and to pound the ground wire below grade.

Do you guys normally do this? I hope it doesn't sound like an amateur question.


Work Gear for Electricians and the Trades

#5044 - 10/30/01 02:14 PM Re: didn't pass inspection, your thoughts  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
If the grounding electrode conductor is #4 or smaller, it may require protection. See 250-64(b). If the ground rod was an 8' rod, it must be completely below grade. See 250-52(c). If you didn't drive 2 rods or use a ground resistance tester to verify compliance with 250-56, the inspector should have also told you to add a second ground rod.
Don(resqcapt19)


Don(resqcapt19)

#5045 - 10/30/01 03:51 PM Re: didn't pass inspection, your thoughts  
bordew  Offline
Member
Joined: Aug 2001
Posts: 142
Vienna,Ohio, USA
electricj:
We are required to run all the grounding conducctors to the disconnect.
For 100 amp service I use a no. 6 bare copper and all it has to do is follow the contour of the building. In fact for any ground rod use no.6, this is in the code.
To the water line thats different No.6 for 100 and 150 amp service and No.4 for a 200 amp service, etc
And of course bury the ground rods spaced at least 6 feet apart.


#5046 - 10/30/01 09:29 PM Re: didn't pass inspection, your thoughts  
spkjpr  Offline
Member
Joined: Dec 2000
Posts: 218
Sedalia,MO, USA
Electricj, don't feel bad my inspector gigged me on that too. Just all at once he got real picky on the rod being below grade. Also I use PVC conduit so there is no need to bond the wire to the conduit. It all happened after he came back from a seminar on grounding.


#5047 - 10/31/01 01:31 PM Re: didn't pass inspection, your thoughts  
electricj  Offline
Member
Joined: Aug 2001
Posts: 10
Boston, MA, USA
spkjpr - Should I just run the pvc out of the meter and then straight into the earth and then let the wire stay underground until it connects to the ground rod? Or would I need to run the pvc (underground) right up to the ground rod?

Thanks for all the replies -- I guess in the future I should also pound down 2 ground rods.


#5048 - 10/31/01 10:56 PM Re: didn't pass inspection, your thoughts  
spkjpr  Offline
Member
Joined: Dec 2000
Posts: 218
Sedalia,MO, USA
Electricj, I run the conduit to ground level out of the meter base then run the ground wire under the soil to the rod. This seems to be accepted here and protects and hides the ground wire. Hope this helps. We are also required to put in 2 ground rods no closer than 6 ft and they must be bonded together.


#5049 - 11/01/01 09:06 AM Re: didn't pass inspection, your thoughts  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
When you drive your rods below grade, be sure to use connectors with "DB" (direct burial) ratings, or use exothermic welding.


#5050 - 11/03/01 01:05 PM Re: didn't pass inspection, your thoughts  
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
It's always a good idea to install two ground rods. It's the maximum number required for a service. However, is it a<b> NEC</b> requirement if only one has a resistance to ground of 25 ohms or less? I am aware that a Power Company can mandate two.


#5051 - 11/03/01 04:58 PM Re: didn't pass inspection, your thoughts  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Frank,
250-56 requires a second rod if the first one is ovr 25 ohms.
Don(resqcapt19)


Don(resqcapt19)

#5052 - 11/11/01 10:36 PM Re: didn't pass inspection, your thoughts  
WireWrestler  Offline
Member
Joined: Oct 2001
Posts: 45
Northern IL
I was red tagged recently in a jurisdiction where I don't work often for running the GEC (bare #6 copper)from the GE, through the neutral lug "bullseye", then through the grounding bushing on the 1 1/4" pipe, and then on into the panel with the service conductors, to the ground bar. His beef was that the bare copper was too close to live lugs. He required me to pull the GEC out of the neutral lug and run an insulated #6 jumper from the grounding bushing to the neutral lug "bullseye". Everywhere else that I work inspectors demand that the GEC be unbroken and continous per code. What do you think. Comments will be appreciated. I have been a long time reader and I enjoy everyone's comments. This is my first reply. I am going to try to participate often.


Page 1 of 2 1 2

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.003s) Memory: 0.8188 MB (Peak: 0.9944 MB) Zlib enabled. Server Time: 2017-04-28 16:07:17 UTC