didn't pass inspection, your thoughts #5043 10/30/01 01:30 PM
Joined: Aug 2001
Posts: 10
E
electricj Offline OP
Member
I did a service last week (hadn't done one in 8 years prior) I had pounded in a ground rod by the meter and ran a ground wire into the meter. I was told to come back and run the wire inside a pipe and to pound the ground wire below grade.

Do you guys normally do this? I hope it doesn't sound like an amateur question.

Work Gear for Electricians and the Trades
Re: didn't pass inspection, your thoughts #5044 10/30/01 02:14 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
If the grounding electrode conductor is #4 or smaller, it may require protection. See 250-64(b). If the ground rod was an 8' rod, it must be completely below grade. See 250-52(c). If you didn't drive 2 rods or use a ground resistance tester to verify compliance with 250-56, the inspector should have also told you to add a second ground rod.
Don(resqcapt19)


Don(resqcapt19)
Re: didn't pass inspection, your thoughts #5045 10/30/01 03:51 PM
Joined: Aug 2001
Posts: 142
B
bordew Offline
Member
electricj:
We are required to run all the grounding conducctors to the disconnect.
For 100 amp service I use a no. 6 bare copper and all it has to do is follow the contour of the building. In fact for any ground rod use no.6, this is in the code.
To the water line thats different No.6 for 100 and 150 amp service and No.4 for a 200 amp service, etc
And of course bury the ground rods spaced at least 6 feet apart.

Re: didn't pass inspection, your thoughts #5046 10/30/01 09:29 PM
Joined: Dec 2000
Posts: 218
S
spkjpr Offline
Member
Electricj, don't feel bad my inspector gigged me on that too. Just all at once he got real picky on the rod being below grade. Also I use PVC conduit so there is no need to bond the wire to the conduit. It all happened after he came back from a seminar on grounding.

Re: didn't pass inspection, your thoughts #5047 10/31/01 01:31 PM
Joined: Aug 2001
Posts: 10
E
electricj Offline OP
Member
spkjpr - Should I just run the pvc out of the meter and then straight into the earth and then let the wire stay underground until it connects to the ground rod? Or would I need to run the pvc (underground) right up to the ground rod?

Thanks for all the replies -- I guess in the future I should also pound down 2 ground rods.

Re: didn't pass inspection, your thoughts #5048 10/31/01 10:56 PM
Joined: Dec 2000
Posts: 218
S
spkjpr Offline
Member
Electricj, I run the conduit to ground level out of the meter base then run the ground wire under the soil to the rod. This seems to be accepted here and protects and hides the ground wire. Hope this helps. We are also required to put in 2 ground rods no closer than 6 ft and they must be bonded together.

Re: didn't pass inspection, your thoughts #5049 11/01/01 09:06 AM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
When you drive your rods below grade, be sure to use connectors with "DB" (direct burial) ratings, or use exothermic welding.

Re: didn't pass inspection, your thoughts #5050 11/03/01 01:05 PM
Joined: Jul 2001
Posts: 311
F
Frank Cinker Offline
Member
It's always a good idea to install two ground rods. It's the maximum number required for a service. However, is it a<b> NEC</b> requirement if only one has a resistance to ground of 25 ohms or less? I am aware that a Power Company can mandate two.

Re: didn't pass inspection, your thoughts #5051 11/03/01 04:58 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Frank,
250-56 requires a second rod if the first one is ovr 25 ohms.
Don(resqcapt19)


Don(resqcapt19)
Re: didn't pass inspection, your thoughts #5052 11/11/01 10:36 PM
Joined: Oct 2001
Posts: 45
W
WireWrestler Offline
Member
I was red tagged recently in a jurisdiction where I don't work often for running the GEC (bare #6 copper)from the GE, through the neutral lug "bullseye", then through the grounding bushing on the 1 1/4" pipe, and then on into the panel with the service conductors, to the ground bar. His beef was that the bare copper was too close to live lugs. He required me to pull the GEC out of the neutral lug and run an insulated #6 jumper from the grounding bushing to the neutral lug "bullseye". Everywhere else that I work inspectors demand that the GEC be unbroken and continous per code. What do you think. Comments will be appreciated. I have been a long time reader and I enjoy everyone's comments. This is my first reply. I am going to try to participate often.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 236
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,060 Are you busy
205,042 Re: Forum
193,167 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3