Laundry Circuit #18599
12/11/02 07:29 PM
12/11/02 07:29 PM
M
master44  Offline OP
Member
Joined: Dec 2002
Posts: 13
Clay Center, Kansas USA
How do you interput 210.11 c (2) It says that the laundry circuit can only supply the laundry receptacle (S). But then it it says . This circuit shall have no other outlets. I was under the opinion that there could be one other recpetacle for an iron ect. It seems to me to be contradict itslf in the same paragraph. Let me know what you do in your area. Thanks Guys and of course you gals too.

Work Gear for Electricians and the Trades
Re: Laundry Circuit #18600
12/11/02 07:40 PM
12/11/02 07:40 PM
S
spyder  Offline
Member
Joined: Oct 2002
Posts: 210
Massachusetts
It means you can't pick up lighting, recptacles in another room off this 20 amp branch circuit. The circuit can only be used for the laundry.

Re: Laundry Circuit #18601
12/11/02 07:42 PM
12/11/02 07:42 PM
C
CTwireman  Offline
Member
Joined: Feb 2002
Posts: 840
Connecticut, USA
I believe the intent of the rule is that the laundry cicuit shall supply no other outlets outside of the laundry room or area.


Peter
Re: Laundry Circuit #18602
12/11/02 07:46 PM
12/11/02 07:46 PM
M
master44  Offline OP
Member
Joined: Dec 2002
Posts: 13
Clay Center, Kansas USA
What if they were going to set up an ironing board in close proximity to the laundry closet but was not in the closet but around the corner in the other room. Would it be ok to have this receptacle on the laundry circuit.

Re: Laundry Circuit #18603
12/11/02 08:16 PM
12/11/02 08:16 PM
S
spyder  Offline
Member
Joined: Oct 2002
Posts: 210
Massachusetts
master 44,

I would say no.

Re: Laundry Circuit #18604
12/11/02 08:43 PM
12/11/02 08:43 PM
T
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
210.11 (C)(2) says....shall be provided to supply the bathroom receptacle outlet(s) required by 210.52(F)....

The subtitle of 210.52 (F) is Laundry Areas

As CTwireman said
Quote
or area


If I was the AHJ I would allow it, but that's just me. master44, give the AHJ a call, and tell them the circumstances, and if they give you a hard time ask them to "waive" it. Remember 90.4 Enforcement.

Waiving Good-Bye, and good luck,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX
Re: Laundry Circuit #18605
12/12/02 04:41 AM
12/12/02 04:41 AM
L
lwinter31  Offline
Member
Joined: Nov 2002
Posts: 40
Texas
I believe it is the code panel's intention to make plural the application of 210.11 c (2) to all [210.52 (F) laundry area(s)] not the "receptacle outlet" that is sigular in (F)
Futhermore a typical washer is rated @ 10a, a typicle iron @1200va. I think a washer running and ironing clothes is a common occurence. This will skim the teeth of "noncontinuous - equal to" of 210.19 (a)

I always dedicate the laundry "washer" receptacle outlet.

Re: Laundry Circuit #18606
12/12/02 10:41 AM
12/12/02 10:41 AM
S
SJT  Offline
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
I would agree. That is to run the washer by it's self. It's possible that the owner may get
a gas dryer. Also that could be plugged into the same ckt. I would set up 2 single outlets for that with 1-20 amp. circuit. The iron and washer going together may trip the breaker. Why take a chance?

Re: Laundry Circuit #18607
12/13/02 07:28 PM
12/13/02 07:28 PM
G
GEC-1  Offline
Member
Joined: Jun 2001
Posts: 32
Covington, Georgia USA
If I was wiring this, I would pull 12/3 to the laundry room. One hot for the washer, and one hot for the iron. If you put the two circuits on different phases, the two can share the neutral. ( the neutral has to be rated to carry the difference of the unbalanced load) Now you have one wire pulled for the two applications. It's also a good way to reduce the number of homeruns you pull in a house.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
Potseal 15
sparky 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,862 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 14 (0.003s) Memory: 0.9990 MB (Peak: 1.1674 MB) Zlib enabled. Server Time: 2018-01-22 18:23:14 UTC