AC UNIT #14664
09/27/02 07:17 AM
09/27/02 07:17 AM
E
EVAD7  Offline OP
Member
Joined: Mar 2002
Posts: 37
MN
WE RECENTLY HOOKED-UP A CENTRAL AC UNIT FOR A CHURCH. IT REPLACED AN EXISTING UNIT. THE AMP DRAW WAS SIMILAR (35 AMPS AT 240 VOLT 1 PH). NOW A PROBLEM HAS DEVELOPED AT START UP, LIGHTS DIM. ANY SOLUTIONS?

Work Gear for Electricians and the Trades
Re: AC UNIT #14665
09/27/02 08:13 AM
09/27/02 08:13 AM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Verify all terminations are tight. Verify the unit is drawing the rated load. Verify conductors are rated properly. Then punt.


Ron
Re: AC UNIT #14666
09/27/02 11:26 AM
09/27/02 11:26 AM
J
JPB  Offline
Junior Member
Joined: Sep 2002
Posts: 3
Westford MA USA
Maybe it has nothing to do with the new A/C.
Could be a coincidence.(Did I spell that right?)
Check for voltage drop at the main.

Re: AC UNIT #14667
09/27/02 05:33 PM
09/27/02 05:33 PM
F
frank  Offline
Member
Joined: May 2001
Posts: 376
windsor ontario canada
Id put on a clamp on with a hold feature to check the LRA on start up,check all lugs and terminations at both the unit and the panel.A slight dimming for a split second seems to be normal in some small services.Locked rotor on that unit can be 210 amps and last longer if the unit starts and stops within 5 minutes beacuse of the high head pressure and the time it takes for the compressor O/L to open if it does not start. good luck explaining this to the owner.Check\replace the compressor capacitor.Caps Can test as good and still fail under load a pretty cheap part to replace as well.

[This message has been edited by frank (edited 09-27-2002).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,917
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
sparky 20
Admin 20
Potseal 13
Popular Topics(Views)
243,537 Are you busy
180,340 Re: Forum
170,829 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.004s) Memory: 0.9573 MB (Peak: 1.0887 MB) Zlib enabled. Server Time: 2018-01-18 16:01:18 UTC