Posted By: EVAD7 AC UNIT - 09/27/02 12:17 PM
WE RECENTLY HOOKED-UP A CENTRAL AC UNIT FOR A CHURCH. IT REPLACED AN EXISTING UNIT. THE AMP DRAW WAS SIMILAR (35 AMPS AT 240 VOLT 1 PH). NOW A PROBLEM HAS DEVELOPED AT START UP, LIGHTS DIM. ANY SOLUTIONS?
Posted By: Ron Re: AC UNIT - 09/27/02 01:13 PM
Verify all terminations are tight. Verify the unit is drawing the rated load. Verify conductors are rated properly. Then punt.
Posted By: JPB Re: AC UNIT - 09/27/02 04:26 PM
Maybe it has nothing to do with the new A/C.
Could be a coincidence.(Did I spell that right?)
Check for voltage drop at the main.
Posted By: frank Re: AC UNIT - 09/27/02 10:33 PM
Id put on a clamp on with a hold feature to check the LRA on start up,check all lugs and terminations at both the unit and the panel.A slight dimming for a split second seems to be normal in some small services.Locked rotor on that unit can be 210 amps and last longer if the unit starts and stops within 5 minutes beacuse of the high head pressure and the time it takes for the compressor O/L to open if it does not start. good luck explaining this to the owner.Check\replace the compressor capacitor.Caps Can test as good and still fail under load a pretty cheap part to replace as well.

[This message has been edited by frank (edited 09-27-2002).]