Id put on a clamp on with a hold feature to check the LRA on start up,check all lugs and terminations at both the unit and the panel.A slight dimming for a split second seems to be normal in some small services.Locked rotor on that unit can be 210 amps and last longer if the unit starts and stops within 5 minutes beacuse of the high head pressure and the time it takes for the compressor O/L to open if it does not start. good luck explaining this to the owner.Check\replace the compressor capacitor.Caps Can test as good and still fail under load a pretty cheap part to replace as well.