#138772 - 09/27/03 01:56 PM Zs + Ze values  
james S  Offline
Member
Joined: May 2003
Posts: 107
West England
when looking at table 2a 7671 on site guide, the value stated for earth fault loop impedance using a bs 3036 fuse 45 amp with a protective conductor of 2.5to 16.0 is o.50ohms. now then at the begining of the guide it states the following Ze values
TN-S system 0.8ohms
TN-C-S system 0.35ohms
TT system 21 ohms
does this then mean that the 45 amp fuse can only be installed in TN-C-S systems due to the Ze values in the other systems are already to high without even taken in to account the circuits cpc?

this goes for all the stated values lower than 0.8ohms using other types of fuse.


Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#138773 - 09/27/03 08:38 PM Re: Zs + Ze values  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
You can still use a 45A fuse or MCB on any of the three systems.

The Regs. specify that in the event of an earth fault a protective device must open the circuit within a certain length of time (most commonly 0.4 sec. for general-purpose outlets and 5 sec. for fixed appliances).

If the loop impedance is not sufficiently low for the OCPD to meet this disconnect time, then you need to add earth-fault protection in the form of an RCD.

In the case of the quoted TT system at around 21 ohms, the fault current on a dead short to earth would be only a little over 11A, so the 45A fuse alone would offer no protection whatsoever.


#138774 - 09/28/03 07:38 AM Re: Zs + Ze values  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Folks,
We seem to have suffered a software glitch on this thread which has left the replies field out by one count.

Bill has tried the various re-build options available on the forum software, but no luck.

Exit stage left, muttering "We don't have bugs, we have undocumented features..." [Linked Image]



Member Spotlight
Admin
Admin
NY, USA
Posts: 3,439
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 14 (0.002s) Memory: 0.7501 MB (Peak: 0.8746 MB) Zlib enabled. Server Time: 2017-04-23 15:51:07 UTC