Zs + Ze values #138772 09/27/03 01:56 PM
Joined: May 2003
Posts: 107
J
james S Offline OP
Member
when looking at table 2a 7671 on site guide, the value stated for earth fault loop impedance using a bs 3036 fuse 45 amp with a protective conductor of 2.5to 16.0 is o.50ohms. now then at the begining of the guide it states the following Ze values
TN-S system 0.8ohms
TN-C-S system 0.35ohms
TT system 21 ohms
does this then mean that the 45 amp fuse can only be installed in TN-C-S systems due to the Ze values in the other systems are already to high without even taken in to account the circuits cpc?

this goes for all the stated values lower than 0.8ohms using other types of fuse.

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: Zs + Ze values #138773 09/27/03 08:38 PM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline
Member
You can still use a 45A fuse or MCB on any of the three systems.

The Regs. specify that in the event of an earth fault a protective device must open the circuit within a certain length of time (most commonly 0.4 sec. for general-purpose outlets and 5 sec. for fixed appliances).

If the loop impedance is not sufficiently low for the OCPD to meet this disconnect time, then you need to add earth-fault protection in the form of an RCD.

In the case of the quoted TT system at around 21 ohms, the fault current on a dead short to earth would be only a little over 11A, so the 45A fuse alone would offer no protection whatsoever.

Re: Zs + Ze values #138774 09/28/03 07:38 AM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline
Member
Folks,
We seem to have suffered a software glitch on this thread which has left the replies field out by one count.

Bill has tried the various re-build options available on the forum software, but no luck.

Exit stage left, muttering "We don't have bugs, we have undocumented features..." [Linked Image]


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,961
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,736 Are you busy
204,966 Re: Forum
193,081 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3