#113292 - 04/09/02 12:28 AM No Main Breaker?  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,439
NY, USA
[Linked Image]

Was this panelboard legal for use as Service Equipment? If so, were there any restrictions? There was no label inside the cover.

Bill


Tools for Electricians:

#113293 - 04/09/02 06:08 AM Re: No Main Breaker?  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,306
with a 4th wire....maybe


#113294 - 04/09/02 08:18 AM Re: No Main Breaker?  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
Sparky,

If you look at the lower Buss there are 12 spaces there. This panel could easily (and did) exceed the maximum # of disconnects. The only way it could comply would be with all 2 pole breakers installed there and that's not likely to happen.

Bill


#113295 - 04/09/02 09:06 AM Re: No Main Breaker?  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
This "split-bus" panel typically has 6 double-pole breakers as the "power section" feeding the range, dryer, AC, etc. Also, a 50 or 60 amp breaker to feed the "lighting" section in the top half. Used in this manner, it would meet the "six operations of the hand" rule with regard to Servive Disconnect.
However, if it is considered a lighting & appliance panel (which it probablty is) it would require a main.
Correct?


#113296 - 04/09/02 09:36 AM Re: No Main Breaker?  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
I still don't understand the advantages of a split bus...

Assuming the bus is protected at 200A, the "sub" breaker feeding the smaller bus is redundant, takes up space, and seems just plain silly...

If there is an advantage, can we have this advantage in the extreme? Let's have a split bus and a sub-feed breaker for every circuit!

(See my point?)


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

#113297 - 04/09/02 11:26 AM Re: No Main Breaker?  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
Bill,

This was suitable for use as Service Equipment. From your photo, the lower 12 pole section was for the "Mains" (before we started calling them Service Disconnects). Then, as now, there could only be a maximum total of six operations of the hand to disconnect the service from the load (up to 6 single poles breakers, 6 double pole or a mixture totalling to a max of 6). The size of the service conductors were based on the calculated load at the time of installation, plus any room for expansion that may, or may not, have been added.

I look at this photo and see it as upside down. I helped install a lot of residential split-bus panels when I was apprenticing.

Even with the "Lighting Section" bus being rated for tandem breakers, over time, I've seen these fill up, and the "open spaces" in the "Main Section" mistakenly (or deliberately) used for branch circuits.

As always, there's no accounting for those who will do anything to get the job done quick and cheaply.

Al


Al Hildenbrand

#113298 - 04/09/02 11:41 AM Re: No Main Breaker?  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
'66

The real attraction to this was the lower material cost. I remember a lot of GE panels, bus only, not a single breaker in them. The leads to the "Lighting Section" were factory installed, but the choice of breaker was up to the installing electrician. If all the "Mains" are 70 Amp or smaller, the higher cost breakers are not used.

Al


Al Hildenbrand

#113299 - 04/09/02 03:19 PM Re: No Main Breaker?  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
Al,

I see it as upside-down too. I see quite a few panelboards (even with main) installed upside-down presumably to save a few feet of cable. I don't remember seeing ones like this with so many spaces (12). Can you tell if this neutral bar is bonded? I don't see a strap.

I don't thonk this was the original panelboard for this house, It was most likely a 100A originally because there was a #6 solid Al cut just above the panel and a #4 Al running to the water main.

Bill


#113300 - 04/09/02 04:01 PM Re: No Main Breaker?  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
spark,

The bus isn't protected at 200 amp. It is not protected at all. These panels are fed directly from the meter. They were not sub-panels. I guess the cost advantage was in not supplying a 200 amp main breaker.


#113301 - 04/09/02 07:38 PM Re: No Main Breaker?  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,306
I mistook it for a mis-wired sub......
[Linked Image]


Page 1 of 2 1 2

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.002s) Memory: 0.8175 MB (Peak: 0.9929 MB) Zlib enabled. Server Time: 2017-04-27 11:09:04 UTC