No Main Breaker? #113292
04/08/02 11:28 PM
04/08/02 11:28 PM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,481
NY, USA
[Linked Image]

Was this panelboard legal for use as Service Equipment? If so, were there any restrictions? There was no label inside the cover.

Bill

Tools for Electricians:
Re: No Main Breaker? #113293
04/09/02 05:08 AM
04/09/02 05:08 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,344
with a 4th wire....maybe

Re: No Main Breaker? #113294
04/09/02 07:18 AM
04/09/02 07:18 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,890
NY, USA
Sparky,

If you look at the lower Buss there are 12 spaces there. This panel could easily (and did) exceed the maximum # of disconnects. The only way it could comply would be with all 2 pole breakers installed there and that's not likely to happen.

Bill

Re: No Main Breaker? #113295
04/09/02 08:06 AM
04/09/02 08:06 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
This "split-bus" panel typically has 6 double-pole breakers as the "power section" feeding the range, dryer, AC, etc. Also, a 50 or 60 amp breaker to feed the "lighting" section in the top half. Used in this manner, it would meet the "six operations of the hand" rule with regard to Servive Disconnect.
However, if it is considered a lighting & appliance panel (which it probablty is) it would require a main.
Correct?

Re: No Main Breaker? #113296
04/09/02 08:36 AM
04/09/02 08:36 AM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
I still don't understand the advantages of a split bus...

Assuming the bus is protected at 200A, the "sub" breaker feeding the smaller bus is redundant, takes up space, and seems just plain silly...

If there is an advantage, can we have this advantage in the extreme? Let's have a split bus and a sub-feed breaker for every circuit!

(See my point?)


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: No Main Breaker? #113297
04/09/02 10:26 AM
04/09/02 10:26 AM
E
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
Bill,

This was suitable for use as Service Equipment. From your photo, the lower 12 pole section was for the "Mains" (before we started calling them Service Disconnects). Then, as now, there could only be a maximum total of six operations of the hand to disconnect the service from the load (up to 6 single poles breakers, 6 double pole or a mixture totalling to a max of 6). The size of the service conductors were based on the calculated load at the time of installation, plus any room for expansion that may, or may not, have been added.

I look at this photo and see it as upside down. I helped install a lot of residential split-bus panels when I was apprenticing.

Even with the "Lighting Section" bus being rated for tandem breakers, over time, I've seen these fill up, and the "open spaces" in the "Main Section" mistakenly (or deliberately) used for branch circuits.

As always, there's no accounting for those who will do anything to get the job done quick and cheaply.

Al


Al Hildenbrand
Re: No Main Breaker? #113298
04/09/02 10:41 AM
04/09/02 10:41 AM
E
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
'66

The real attraction to this was the lower material cost. I remember a lot of GE panels, bus only, not a single breaker in them. The leads to the "Lighting Section" were factory installed, but the choice of breaker was up to the installing electrician. If all the "Mains" are 70 Amp or smaller, the higher cost breakers are not used.

Al


Al Hildenbrand
Re: No Main Breaker? #113299
04/09/02 02:19 PM
04/09/02 02:19 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,890
NY, USA
Al,

I see it as upside-down too. I see quite a few panelboards (even with main) installed upside-down presumably to save a few feet of cable. I don't remember seeing ones like this with so many spaces (12). Can you tell if this neutral bar is bonded? I don't see a strap.

I don't thonk this was the original panelboard for this house, It was most likely a 100A originally because there was a #6 solid Al cut just above the panel and a #4 Al running to the water main.

Bill

Re: No Main Breaker? #113300
04/09/02 03:01 PM
04/09/02 03:01 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
spark,

The bus isn't protected at 200 amp. It is not protected at all. These panels are fed directly from the meter. They were not sub-panels. I guess the cost advantage was in not supplying a 200 amp main breaker.

Re: No Main Breaker? #113301
04/09/02 06:38 PM
04/09/02 06:38 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,344
I mistook it for a mis-wired sub......
[Linked Image]

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,583 Are you busy
180,379 Re: Forum
170,856 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 15 (0.004s) Memory: 1.0232 MB (Peak: 1.2001 MB) Zlib enabled. Server Time: 2018-01-21 20:30:33 UTC