** 2002 NEC Section 110.26 Violations Here! ** #104442
02/26/03 06:41 AM
02/26/03 06:41 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
HINT: There are some foreign systems that are installed directly over the equipment.

[Linked Image]

NOTE: As this area is sometimes used as a reference for Vocational studies we request that comments be kept to the subject as much as possible. Thank You for your cooperation in this matter.


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: ** 2002 NEC Section 110.26 Violations Here! ** #104443
02/26/03 11:16 AM
02/26/03 11:16 AM
M
mamills  Offline
Member
Joined: Nov 2001
Posts: 745
Wharton, Texas, USA
Well, to start off, I see what appears to be copper water lines in the area above the switchgear and wire gutter. A run for the hills is in order if the piping springs a leak...

Mike (mamills)

Re: ** 2002 NEC Section 110.26 Violations Here! ** #104444
02/26/03 01:38 PM
02/26/03 01:38 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
While the water pipe is a code violation, I don't really see it as much of a hazard. In my opinion, the roof above the gear is much more likely to leak than is the water pipe.
Don


Don(resqcapt19)
Re: ** 2002 NEC Section 110.26 Violations Here! ** #104445
02/26/03 05:37 PM
02/26/03 05:37 PM
E
Elec_VA  Offline
Member
Joined: Jan 2003
Posts: 40
Sterling, VA, USA
If I remember right, attatching conduit to other conduit does constitute support! The conduit going into the panel in the rear of the photo also seems to be lacking support in a big way! (2 out of 7 supported within 3 feet?)

Also there is the open wireway midway up the right side of the pic.

I hope they didn't think of the rigid arches as nipples, and fill to 60%!

Now onto clearence:
There seems to be conduit directly in front of the hinged cover of a wireway by the previously mentioned copper.

I don't have the bible on me (for shame for shame [Linked Image] ), but I know there a number of subsections relating to overhead clearance. There is language about foreign systems allowed and not allowed to be above electrical equipment. (to quote the hint [Linked Image] ) Can't think of the rules or the exceptions off the top of my head (jost got home from work, the brain's tired [Linked Image] ).

What else am I missing?


Pete
Re: ** 2002 NEC Section 110.26 Violations Here! ** #104446
02/27/03 06:39 PM
02/27/03 06:39 PM
J
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
Heck, that's no surprise. I don't think I've EVER seen a switchgear room that wasn't filled with out-of-season merchandise, didn't have HVAC, Plbg., etc. running through it, and also had both exits usable!
I suppose that the part that puzzles me are the fire sprinklers typically installed above NEMA-1 gear. Overload leads to heat, which trips sprinkler, which begins Great White-type pyrotechnics....

Re: ** 2002 NEC Section 110.26 Violations Here! ** #104447
03/04/03 10:05 PM
03/04/03 10:05 PM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
I don’t see any support for the rigid conduit loops between gutters. Both sets have strut and straps to keep them in line but I do not see any threaded rod up to the structure.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,862 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.9762 MB (Peak: 1.1229 MB) Zlib enabled. Server Time: 2018-01-22 20:07:46 UTC