Joined: Oct 2000
Posts: 2,749
Member
HINT: There are some foreign systems that are installed directly over the equipment.

[Linked Image]

NOTE: As this area is sometimes used as a reference for Vocational studies we request that comments be kept to the subject as much as possible. Thank You for your cooperation in this matter.


Joe Tedesco, NEC Consultant
Insulated Tools for Electricians

Insulated Tools for Electricians, Installers & Maintenance Technicians

Joined: Nov 2001
Posts: 745
M
Member
Well, to start off, I see what appears to be copper water lines in the area above the switchgear and wire gutter. A run for the hills is in order if the piping springs a leak...

Mike (mamills)

Joined: Nov 2000
Posts: 2,148
R
Member
While the water pipe is a code violation, I don't really see it as much of a hazard. In my opinion, the roof above the gear is much more likely to leak than is the water pipe.
Don


Don(resqcapt19)
Joined: Jan 2003
Posts: 40
E
Member
If I remember right, attatching conduit to other conduit does constitute support! The conduit going into the panel in the rear of the photo also seems to be lacking support in a big way! (2 out of 7 supported within 3 feet?)

Also there is the open wireway midway up the right side of the pic.

I hope they didn't think of the rigid arches as nipples, and fill to 60%!

Now onto clearence:
There seems to be conduit directly in front of the hinged cover of a wireway by the previously mentioned copper.

I don't have the bible on me (for shame for shame [Linked Image] ), but I know there a number of subsections relating to overhead clearance. There is language about foreign systems allowed and not allowed to be above electrical equipment. (to quote the hint [Linked Image] ) Can't think of the rules or the exceptions off the top of my head (jost got home from work, the brain's tired [Linked Image] ).

What else am I missing?


Pete
Joined: Apr 2001
Posts: 518
J
Member
Heck, that's no surprise. I don't think I've EVER seen a switchgear room that wasn't filled with out-of-season merchandise, didn't have HVAC, Plbg., etc. running through it, and also had both exits usable!
I suppose that the part that puzzles me are the fire sprinklers typically installed above NEMA-1 gear. Overload leads to heat, which trips sprinkler, which begins Great White-type pyrotechnics....

Joined: Aug 2001
Posts: 599
N
Member
I don’t see any support for the rigid conduit loops between gutters. Both sets have strut and straps to keep them in line but I do not see any threaded rod up to the structure.