0 members (), 150 guests, and 35 robots.
#99075 07/13/06 07:11 PM
Does 110.26(F) apply to a anything else besides the item listed in the article?
Second question - Does 110.26(A) apply to J-boxes?
George Little
Workgear for Electricians
#99076 07/13/06 07:20 PM
Y
How would you do the Job?? Just items mentioned in code section I;d say. Nope/\
#99077 07/13/06 10:17 PM
Where are you heading with this?
~~ CELTIC ~~
...-= NJ =-...
#99078 07/13/06 11:39 PM
e57 Offline
"Sufficient access and working space shall be provided and maintained about all electric equipment to permit ready and safe operation and maintenance of such equipment."
Is what it says first, and later lists the parameters....
"Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized..." - You can shut off a box, and it very unlikely that you would need to do all of those things hot, like you might for a panel, especially a main panel. As far as "F" goes, I (Can't) think of anything else...
[This message has been edited by e57 (edited 07-14-2006).]
#99079 07/14/06 12:14 AM
I never quite understood why an HVAC disconnect needed to be serviced while energized but I have always been told it needed full working space.
If we changed the rule on that the world would spin out of orbit, into the universe and life as we know it would cease ... or so we have been led to believe.
#99080 07/14/06 12:23 AM
I just popped up the same question over at the IAEI board. Lets see what they say
#99081 07/14/06 08:49 AM
As E57 refers to; does it need servicing, adjustment, etc. while energized ?
A large J box with contactors in it or something like that would be a yes, otherwise no.
Alan--
Alan--