Does 110.26(F) apply to a anything else besides the item listed in the article?

Second question - Does 110.26(A) apply to J-boxes?


George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#99076 07/13/06 07:20 PM
Joined: Mar 2003
Posts: 849
Y
Member
How would you do the Job?? Just items mentioned in code section I;d say. Nope/\

#99077 07/13/06 10:17 PM
Joined: Feb 2005
Posts: 361
C
Member
Where are you heading with this?


~~ CELTIC ~~
...-= NJ =-...
#99078 07/13/06 11:39 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
"Sufficient access and working space shall be provided and maintained about all electric equipment to permit ready and safe operation and maintenance of such equipment."

Is what it says first, and later lists the parameters....

"Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized..." - You can shut off a box, and it very unlikely that you would need to do all of those things hot, like you might for a panel, especially a main panel. As far as "F" goes, I (Can't) think of anything else...

[This message has been edited by e57 (edited 07-14-2006).]


Mark Heller
"Well - I oughta....." -Jackie Gleason
#99079 07/14/06 12:14 AM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I never quite understood why an HVAC disconnect needed to be serviced while energized but I have always been told it needed full working space.
If we changed the rule on that the world would spin out of orbit, into the universe and life as we know it would cease ... or so we have been led to believe.


Greg Fretwell
#99080 07/14/06 12:23 AM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I just popped up the same question over at the IAEI board. Lets see what they say


Greg Fretwell
#99081 07/14/06 08:49 AM
Joined: Mar 2005
Posts: 399
A
Member
As E57 refers to; does it need servicing, adjustment, etc. while energized ?
A large J box with contactors in it or something like that would be a yes, otherwise no.
Alan--


Alan--
If it was easy, anyone could do it.