water main #98838
06/15/06 09:18 PM
06/15/06 09:18 PM
S
Sparks30  Offline OP
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
It's been a while since I have done a 200 amp service, I'll be using 4/0 AL for service. #6 to ground rods. Does the water main get #4 ? Sorry to sound stupid just having one of those days.

2017 / 2014 NEC & Related Books and Study Guides
Re: water main #98839
06/15/06 09:48 PM
06/15/06 09:48 PM
C
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
6 for the ground is ok check 250.66

Re: water main #98840
06/15/06 09:56 PM
06/15/06 09:56 PM
S
Sparks30  Offline OP
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
250.66 says 4/0 AL with copper ground is #4. Or am I reading wrong?

Re: water main #98841
06/15/06 10:16 PM
06/15/06 10:16 PM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
#4 copper to the water main will be fine, and meets code per NEC.

Re: water main #98842
06/15/06 10:29 PM
06/15/06 10:29 PM
S
Sparks30  Offline OP
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
If I can run a #6 I will do that any wire I do not have to buy at these prices will help.

Re: water main #98843
06/15/06 10:37 PM
06/15/06 10:37 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,343
Estero,Fl,usa
The ground rod conductor can be #6 but you still have to bond the pipe with #4.


Greg Fretwell
Re: water main #98844
06/16/06 09:38 AM
06/16/06 09:38 AM
C
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
oppps


I didn't catch the reference to the water pipe. Sorry

as gfretwell stated.
Interior water pipe requires a # 4 The rods are fine with the #6.


Sorry again


Charlie


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,151
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Albert 3
Popular Topics(Views)
253,837 Are you busy
190,299 Re: Forum
179,996 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 15 (0.005s) Memory: 0.9823 MB (Peak: 1.1369 MB) Zlib enabled. Server Time: 2019-03-18 19:43:52 UTC