#98838 - 06/15/06 09:18 PM water main  
Sparks30  Offline
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
It's been a while since I have done a 200 amp service, I'll be using 4/0 AL for service. #6 to ground rods. Does the water main get #4 ? Sorry to sound stupid just having one of those days.


2017 / 2014 NEC & Related Books and Study Guides

#98839 - 06/15/06 09:48 PM Re: water main  
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
6 for the ground is ok check 250.66


#98840 - 06/15/06 09:56 PM Re: water main  
Sparks30  Offline
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
250.66 says 4/0 AL with copper ground is #4. Or am I reading wrong?


#98841 - 06/15/06 10:16 PM Re: water main  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
#4 copper to the water main will be fine, and meets code per NEC.


#98842 - 06/15/06 10:29 PM Re: water main  
Sparks30  Offline
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
If I can run a #6 I will do that any wire I do not have to buy at these prices will help.


#98843 - 06/15/06 10:37 PM Re: water main  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,122
Estero,Fl,usa
The ground rod conductor can be #6 but you still have to bond the pipe with #4.


Greg Fretwell

#98844 - 06/16/06 09:38 AM Re: water main  
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
oppps


I didn't catch the reference to the water pipe. Sorry

as gfretwell stated.
Interior water pipe requires a # 4 The rods are fine with the #6.


Sorry again


Charlie



Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.7828 MB (Peak: 0.9372 MB) Zlib enabled. Server Time: 2017-10-18 10:52:36 UTC