It's been a while since I have done a 200 amp service, I'll be using 4/0 AL for service. #6 to ground rods. Does the water main get #4 ? Sorry to sound stupid just having one of those days.
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#98839 06/15/06 09:48 PM
6 for the ground is ok check 250.66
#98840 06/15/06 09:56 PM
250.66 says 4/0 AL with copper ground is #4. Or am I reading wrong?
#98841 06/15/06 10:16 PM
#4 copper to the water main will be fine, and meets code per NEC.
#98842 06/15/06 10:29 PM
If I can run a #6 I will do that any wire I do not have to buy at these prices will help.
#98843 06/15/06 10:37 PM
The ground rod conductor can be #6 but you still have to bond the pipe with #4.