200A service with 4/0 alum. cond. what size GEC is okay? i know that table 250.66 says #4 but im in an arguement with someone who says it's not required to be any larger than #6. also, there is no rebar ground and plastic water service. what do you say?

Work Gear for Electricians and the Trades

Workgear for Electricians

#98541 05/31/06 10:43 PM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
250.66(A) says #6.

#98542 05/31/06 11:35 PM
Joined: Feb 2005
Posts: 693
L
Member
A driven ground never needs more than #6 cu. Any other electrode, #4 cu.