Posted By: hedlok GEC sizing - 06/01/06 02:32 AM
200A service with 4/0 alum. cond. what size GEC is okay? i know that table 250.66 says #4 but im in an arguement with someone who says it's not required to be any larger than #6. also, there is no rebar ground and plastic water service. what do you say?
Posted By: Bob Re: GEC sizing - 06/01/06 02:43 AM
250.66(A) says #6.
Posted By: Larry Fine Re: GEC sizing - 06/01/06 03:35 AM
A driven ground never needs more than #6 cu. Any other electrode, #4 cu.