0 members (), 2,389 guests, and 228 robots.
#98332 05/30/06 02:21 AM
e57 Offline
Dear Devil's Advocate,
210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. Receptacle outlets required by this section shall be in addition to any receptacle that is part of a luminaire (lighting fixture) or appliance, located within cabinets or cupboards, or located more than 1.7 m (51/2 ft) above the floor.
Some of the systems accociated with home automation coud be considered appliances, and intended as control of a luminaire only. If the outlet is not available for any other use than lighting, doesn't that make it a lighting outlet?
Receptacle outlets are defined diffeently than lighting outlets.
Workgear for Electricians
#98333 05/30/06 08:23 AM
Okay. Define those receptacle outlets, and show where it states that they must accept a particular receptacle configuration.
Larry Fine
Fine Electric Co.
fineelectricco.com
#98334 05/30/06 09:05 AM
Okay Larry- Put the inspector hat on - go to court, explain to the judge why Mrs. Homeowner don't have a place to plug in her TV or her Vacuum Cleaner unless she changes the cap on the cord. Get real Larry, your just messin with us. [Linked Image]
George Little
#98335 05/30/06 09:23 PM
e57 Offline
It's not the configuration.... It's the fact that it is powered by a dimmer... A switched outlet is one thing, a dimmed outlet is another. By proxy it becomes part of the lighting system. Plug a vaccum or a computer into it and it may not be so nice. As it is not usable as a 15-20A outlet, IMO it does not count as one, it is a lighting outlet.... As the cord cap for them is described here. http://www.lutron.com/applicationnotes/048085b.pdf
"The DFDU and HFDU receptacles with the RP-FDU plug are UL listed for use with
specific Lutron dimmers for the control of portable lamps."
However a 1/2 dimmed would....