New Romex cable #9825
05/15/02 11:47 AM
05/15/02 11:47 AM
C
CTwireman  Offline OP
Member
Joined: Feb 2002
Posts: 840
Connecticut, USA
Check out www.southwire.com

Does anyone else think this cable should have been invented a long time ago?


Peter
Work Gear for Electricians and the Trades
Re: New Romex cable #9826
05/15/02 07:34 PM
05/15/02 07:34 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
Quote
"Historically, contractors have used three conductor cables and a shared neutral for two bedroom circuits to reduce the labor costs over installing two cables," explained Dave Mercier, technical director for Southwire’s Electrical Division. "However, with the newly required AFCI breakers for bedrooms, many builders must now use separate neutrals when two circuits are needed. Southwire’s new 2/2/conductor cable with two neutrals solves this problem for the contractor while continuing to offer labor savings and convenience," he added.


would'nt 2P AFCI's be simpler, as well as easy on the box vol, 3 vs. 4 wires...

Re: New Romex cable #9827
05/15/02 08:10 PM
05/15/02 08:10 PM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Is white with a red stripe legal for a neutral?

I do like the new colored jackets; nice design decision.

On a side note: Is copper really cheap for everyone right now? I've been getting Rx 12-2-G for $0.08 per foot, which is a really good price for around here.


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: New Romex cable #9828
05/15/02 08:16 PM
05/15/02 08:16 PM
R
rkukl  Offline
Member
Joined: Oct 2001
Posts: 41
Turners Falls,MA. USA
Great idea leave it to the manufactures to find a way to capitalize on a change we’ve all been moaning over.
Hope my supply house gets some real soon!!!

Re: New Romex cable #9829
05/15/02 08:54 PM
05/15/02 08:54 PM
R
Rabbit  Offline
Member
Joined: Jan 2002
Posts: 64
Kingsport Tennessee
I'm not a residential man but why not just pull two 12/2 w/g's. Just seems like something else to have to buy.

Re: New Romex cable #9830
05/15/02 10:46 PM
05/15/02 10:46 PM
E
Electric Eagle  Offline
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
I've never liked using 3 wire to vrun 2 circuits because you have to use a common trip breaker and later someone thinks its a 220(240) circuit. So if the wire isn't more than 2 times as expensive, I could see using this alot to run home runs in lots of areas. Just think you can run one wire for 2 kitchen small appliance circuits or as Southwire says, 2 bedrooms.

I also like Southwires new color coding, we now can keep our 14 and 12 separate. If they would only make more colors like cat5 has to keep circuits color coded.

Re: New Romex cable #9831
05/15/02 11:28 PM
05/15/02 11:28 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Sparky,
Quote
Is white with a red stripe legal for a neutral?

That is a good question. It appears to me that the stripe is only permitted for a "second system" grounded conductor. Is a grounded conductor for a second circuit a "second system"?
Quote
D) Grounded Conductors of Different Systems. Where conductors of different systems are installed in the same raceway, cable, box, auxiliary gutter, or other type of enclosure, one system grounded conductor, if required, shall have an outer covering conforming to 200.6(A) or 200.6(B). Each other system grounded conductor shall have an outer covering of white with a readily distinguishable, different colored stripe other than green running along the insulation, or shall have other and different means of identification as allowed by 200.6(A) or (B) that will distinguish each system grounded conductor.

Don(resqcapt19)


Don(resqcapt19)
Re: New Romex cable #9832
05/16/02 01:08 AM
05/16/02 01:08 AM
C
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Electric Eagle, you are not required to use a common trip breaker when using three conductor cable for multi-wire circuits.


Curt Swartz
Re: New Romex cable #9833
05/16/02 07:05 AM
05/16/02 07:05 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I like the colored NM cables.
Don,
I know you know this. Different systems refer to different characteristics or sources.
caselec,
If the multi-wire circuit terminates on a single strap in a residential application, a double pole breaker is required.

Re: New Romex cable #9834
05/16/02 08:22 AM
05/16/02 08:22 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Redsy,
So then the use of this cable is a violation of 200.6.
Don(resqcapt19)


Don(resqcapt19)
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006