0 members (), 890 guests, and 12 robots.
#97636 03/10/06 12:28 AM
Has this table changed between 2002-2005? I've been using Stallcup's Master study guide and a question has me stumped. Here is the question "Rigid metal conduit should be buried in the ground at a minimum of __ inches?"
A)4 B)6 C)12 D)18
I am coming up with an answer different than what the study guide says I should get using this table. I am using a 2002 code book,but a 2005 study guide.
Thanks
Nathan
Workgear for Electricians
#97637 03/10/06 12:51 AM
6"?
#97638 03/10/06 12:58 AM
my answer was 4" so is the 2005 table different than the 2002 table?
#97639 03/10/06 06:55 AM
ngoody 24
Table 300.5 is the same (2002 & 2005) in Column 2 (RMC & IMC).
All locations not specified below...6".
Dave
#97640 03/10/06 09:17 PM
That's one of the nice things about using rigid - not having to dig as deep!
#97641 03/11/06 09:07 AM
The 6" cover requirement was first called out in the '71 or '75 NEC, and hasn't changed since.
#97642 03/11/06 11:31 AM
The fine print of the code aside, I like things DEEP. For me, this means a minimum of being a coupl incehs deeper than the bottom of a slab, and deeper than the blade of a shovel (about 12").
Why? Because I don't want the pipe hit every time the gardner plants a flower or fixes a leaky irrigation pipe. I don't want the slab to act like "the worlds' dullest scissors" where the pipe exits. And I don't want the pipe cut when the plumber has to open up the slab to replace a drain.
#97643 03/11/06 12:41 PM
Good point about the plumber. Rigid is tough stuff but no match for a 14" chop saw.