What's the "fix" for a situation where there are cables in a vault that operate in different voltage ranges--like for transformer line/load conductors, one set over 600V and the load side under 600V. In this scenario, the cables are coming into the vault in such a way that there is no way to place a rigid physical barrier between the conductors. Is it practicable to wrap the 600V conductors with high voltage insulation?
I don't know what the Raychem product is that you mentioned. This transformer vault situation is something that someone else had run into recently, I haven't seen the installation myself. My understanding is that you can have shielded URD racked within 6" of the 600V wire, but if it is un-shielded you can't have it in the same enclosure.