ECN Forum

transformer leads of different voltage ratings mixing

Posted By: Elzappr

transformer leads of different voltage ratings mixing - 05/12/02 03:52 AM

What's the "fix" for a situation where there are cables in a vault that operate in different voltage ranges--like for transformer line/load conductors, one set over 600V and the load side under 600V. In this scenario, the cables are coming into the vault in such a way that there is no way to place a rigid physical barrier between the conductors. Is it practicable to wrap the 600V conductors with high voltage insulation?
Posted By: Bjarney

Re: transformer leads of different voltage ratings mixing - 05/12/02 04:27 AM

There is Raychem BBIT but it will cost you plenty. I'd be sure your inspector will buy in to it first.
Posted By: Elzappr

Re: transformer leads of different voltage ratings mixing - 05/12/02 11:57 PM

I don't know what the Raychem product is that you mentioned. This transformer vault situation is something that someone else had run into recently, I haven't seen the installation myself. My understanding is that you can have shielded URD racked within 6" of the 600V wire, but if it is un-shielded you can't have it in the same enclosure.

[This message has been edited by Elzappr (edited 05-12-2002).]