#97490 02/23/06 04:45 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Is there anything in NFPA72 that would require an installer or a design professional to install or design an installation of a fire alarm system to meet the requirements of a Class A circuit?

Secondly- what percent of the systems being installed are Class A?


George Little
Work Gear for Electricians and the Trades

Workgear for Electricians

#97491 02/23/06 06:47 PM
Joined: Dec 2003
Posts: 751
E
Member
I see class 1, 2 & 3 circuits in the NEC, but no class A circuits. What are they?


Earl
#97492 02/23/06 07:49 PM
Joined: Jun 2004
Posts: 220
T
Member
A class A FA system uses return conductors for supervision. A class B uses EOLs for the supervision of the circuits.

I have seen more Class B lately. Last Class A I put in was at the Maine State Prison.

#97493 02/23/06 10:33 PM
Joined: Mar 2003
Posts: 849
Y
Member
George
Your answers on Page 72-41 Chaper 3 (3-4)
1999 NFPA 72.
Most nowadays are Class B Class A requires the outgoing and return conductors to be routed separately and shall Not be run in the same cable assembly. Page 72-41 (3-4.2.2.2*(Note exceptions) on page 74-42

#97494 02/25/06 11:26 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Depends on the type of buildings you work in. More than 50% of the building I work in are Class A due to reliability requirements and occasional slow repair cycles.
Many are not familiar with Class A circuits and they are not specified due to "that's the way I always did it, and it worked that time"


Ron
#97495 02/26/06 02:26 AM
Joined: Nov 2005
Posts: 826
Likes: 1
J
Member
Most of our systems use class B, where you see 2 jumpers in the panel per zone and 2 wires going out. Class A is safer because it can be cut in the middle of the loop and still cause an alarm on either end. A class B intelligent system may not use EOLs because each device is polled so you don't need a resistor, capacitor, or diode at the end to know that you're getting to the last device.