Fire Alarm System #97490
02/23/06 03:45 PM
02/23/06 03:45 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
Is there anything in NFPA72 that would require an installer or a design professional to install or design an installation of a fire alarm system to meet the requirements of a Class A circuit?

Secondly- what percent of the systems being installed are Class A?


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Fire Alarm System #97491
02/23/06 05:47 PM
02/23/06 05:47 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
I see class 1, 2 & 3 circuits in the NEC, but no class A circuits. What are they?


Earl
Re: Fire Alarm System #97492
02/23/06 06:49 PM
02/23/06 06:49 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
A class A FA system uses return conductors for supervision. A class B uses EOLs for the supervision of the circuits.

I have seen more Class B lately. Last Class A I put in was at the Maine State Prison.

Re: Fire Alarm System #97493
02/23/06 09:33 PM
02/23/06 09:33 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
George
Your answers on Page 72-41 Chaper 3 (3-4)
1999 NFPA 72.
Most nowadays are Class B Class A requires the outgoing and return conductors to be routed separately and shall Not be run in the same cable assembly. Page 72-41 (3-4.2.2.2*(Note exceptions) on page 74-42

Re: Fire Alarm System #97494
02/25/06 10:26 PM
02/25/06 10:26 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Depends on the type of buildings you work in. More than 50% of the building I work in are Class A due to reliability requirements and occasional slow repair cycles.
Many are not familiar with Class A circuits and they are not specified due to "that's the way I always did it, and it worked that time"


Ron
Re: Fire Alarm System #97495
02/26/06 01:26 AM
02/26/06 01:26 AM
J
JoeTestingEngr  Offline
Member
Joined: Nov 2005
Posts: 799
Chicago, Il.
Most of our systems use class B, where you see 2 jumpers in the panel per zone and 2 wires going out. Class A is safer because it can be cut in the middle of the loop and still cause an alarm on either end. A class B intelligent system may not use EOLs because each device is polled so you don't need a resistor, capacitor, or diode at the end to know that you're getting to the last device.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,208 Are you busy
189,185 Re: Forum
178,869 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 14 (0.003s) Memory: 0.9762 MB (Peak: 1.1214 MB) Zlib enabled. Server Time: 2018-12-15 07:31:59 UTC